• To anyone looking to acquire commercial radio programming software:

    Please do not make requests for copies of radio programming software which is sold (or was sold) by the manufacturer for any monetary value. All requests will be deleted and a forum infraction issued. Making a request such as this is attempting to engage in software piracy and this forum cannot be involved or associated with this activity. The same goes for any private transaction via Private Message. Even if you attempt to engage in this activity in PM's we will still enforce the forum rules. Your PM's are not private and the administration has the right to read them if there's a hint to criminal activity.

    If you are having trouble legally obtaining software please state so. We do not want any hurt feelings when your vague post is mistaken for a free request. It is YOUR responsibility to properly word your request.

    To obtain Motorola software see the Sticky in the Motorola forum.

    The various other vendors often permit their dealers to sell the software online (i.e., Kenwood). Please use Google or some other search engine to find a dealer that sells the software. Typically each series or individual radio requires its own software package. Often the Kenwood software is less than $100 so don't be a cheapskate; just purchase it.

    For M/A Com/Harris/GE, etc: there are two software packages that program all current and past radios. One package is for conventional programming and the other for trunked programming. The trunked package is in upwards of $2,500. The conventional package is more reasonable though is still several hundred dollars. The benefit is you do not need multiple versions for each radio (unlike Motorola).

    This is a large and very visible forum. We cannot jeopardize the ability to provide the RadioReference services by allowing this activity to occur. Please respect this.

fire station alerting/wiring

Status
Not open for further replies.

ocguard

Member
Joined
Nov 9, 2002
Messages
1,288
Location
PA/MD
I'm looking at doing an overhaul on a portion of the fire station alerting system at work. Our station alerting is accomplished via our Motorola v7 P25 radio system SCADA and ACE3600 RTU. I'm not so much looking at changing anything on the radio end, but what happens after the radio.

Our RTU sends out a low-voltage signal to a vintage Gamewell gong, rings the gong, which is wired in series to an AC relay to activate the lights in the bunkroom and apparatus floor. Problem is, sometimes, the relay never trips. The gong is always consistently works, but the lights are very unreliable.

I know this is more of an electrical issue than a true radio issue, but hopefully someone has the knowledge of what I've described to give me some insight on how to make the entire system work more reliably.
 

krokus

Member
Premium Subscriber
Joined
Jun 9, 2006
Messages
5,992
Location
Southeastern Michigan
Under the KISS principle: Is the relay in good condition? The contacts might be damaged, or windings might have shorted.

When testing relays, make sure they engage at the rated coil voltage, and hold their position, until at least 80% (ish) of their rated coil voltage.

Are you sure the relay and gong are wired in series? That would seem a bit odd. I would think they would be in parallel.
 

ocguard

Member
Joined
Nov 9, 2002
Messages
1,288
Location
PA/MD
Under the KISS principle: Is the relay in good condition? The contacts might be damaged, or windings might have shorted.

When testing relays, make sure they engage at the rated coil voltage, and hold their position, until at least 80% (ish) of their rated coil voltage.

Are you sure the relay and gong are wired in series? That would seem a bit odd. I would think they would be in parallel.

There is only one output leaving the RTU, then is disappears into the wall. At the gong, a wire comes out of the wall to the... solenoid? Or whatever you call that mechanism that trips the gong's actuator. Then goes back into the wall. So I assume they are run in series.
 

W2NJS

Member
Joined
Mar 27, 2006
Messages
1,938
Location
Washington DC
If the light relay is actually in series with the gong then the relay must have the same current draw as the gong. In the series alarm circuits the voltage is additive so the current must be uniform for each device on the circuit. What you most likely need is the services of a good fire alarm technician or an electrician who understands alarm circuitry.
 

ocguard

Member
Joined
Nov 9, 2002
Messages
1,288
Location
PA/MD
If the light relay is actually in series with the gong then the relay must have the same current draw as the gong. In the series alarm circuits the voltage is additive so the current must be uniform for each device on the circuit. What you most likely need is the services of a good fire alarm technician or an electrician who understands alarm circuitry.

We used to have dedicated fire alarm technicians on staff. Now we have Google, chewed bubble gum, and a house fund.
 

Thayne

Member
Joined
May 1, 2002
Messages
2,145
Check what voltage & if it is AC or DC leaving the RTU, (Maybe it comes from a transformer somewhere near) then activate it and check the voltage at the gong, (You can tell if it is series or parallel at that connection) then anyone with some electrical knowledge can figure out where the problem is--bad relay or whatever.
 

902

Member
Joined
Nov 7, 2003
Messages
2,625
Location
Downsouthsomewhere
Just from a quick read, two things come to mind: 1) simultaneous current draw, and 2) inductive "kick" from a solenoid or relay. Some very simple things to try which might negate your need for a PLC replacement - 1) place a diode across the relay/solenoid windings; 2) construct an emitter follower circuit that provides isolation between the two independent systems. No guarantees, but I'd say give it a shot.

Wouldn't the light output line be latched and the gong be momentary or a timed pulse?
 