I think you meant some other value for the wire size than #30, COM19... (an aside, #30 copper wire has a resistance of something like 1 Ohm per 10 feet- the stuff of fusible links
)
But its the placement of the ground wire that struck me. Running as you described it, COM, will be Okay to bleed off light static charges, but anything big, sudden and flashy is going to take the fastest, shortest rounte to the earth; likely thru your roof. That circuitously routed ground wire is going to act more like a big reactance impedence lump (yes, lightning behaves like RF- ) Lightning will ignore it, finding its way to neutral thru the path of least resistance (likely your house wiring, plumbing- metal siding............)
Once upon a time, I got a dramatic, first hand experience with the awesome brute strength of lightning. I was a guest at a high altitude meteorological research station- a station that pokes its nose up tauntingly at Zesus; its high on a mountain top famous for severe weather... ie: lots of lightning.
One of the first things I noticed about this station was the 60 foot tall steel "air terminal"- a cute phrase for a lightning rod- standing about 10 feet from the main building (living quarters, kitchen, instrument room- its not a big building.)
This "air thingy" was no slouch of a lightning rod- the base was 12 inches in diameter- tapering up to 3 or so inches at the top. Several coronal discharge rings festooned its length-- but what really caught my eye were the fuses fixed to the side of the behemoth. They were fusible link fuses commonly used in cars- these were in series, running parallel, with wire leads about 4 inches on either side, attached to large bolts weld'd to the mast.
Can everyone picture these?.. a slight current secondary path thru a fuse that bypassed the main, humongous steel lightning rod by some 8 inches. There were several of these "fuse bypass's"- each with different value'd fuses (5, 10, 20, 30 ! amps.) Imagine the total current thru the mast, if enuff current gets shunted off thru those fuses to blow a 30 amp'r.
Before my visit was over, I got a first row seat performance of the wrath of the gods... an electrical storm par excellence. Everyone in the station sat individually perched on tall wooden stools with ceramic power pole insulators on the stool legs, all this as Zesus hurtled bolt after bolt down at us. When they hit the "air terminal' the whole mast rung like a bell for several seconds. Coronas danced on the outside metal of the building's frame work- no one thought to leave the safety (??) of their stools while the fireworks blaz'd.
Enuff of the colourful imagery-
....When the storm passed, I went outside and looked at those fuses. Every one of them was 'blown !"
One of the researchers said-
"Humpf, maybe we should try higher value fuses next time"
.
Okay Guys- calculate the total current of a lightning bolt that could blow one of those 30 amp fuses while 99.99999% of the rest courses to ground thru the huge metal mast.
Think a piece of #6 wire is going to save anything, even with a puny secondary strike ?
But Hey !, run those wires for static discharges, read all you can about lightning- take a trip to look at a mountain top tele-comm site and see what the pro's do.
And don't taunt the gods
Lauri