Here's the situation. earlier this week I went outside to put up a couple of antennas. This required of course that I ground the mast and coax shield to earth outside.
Well, once I grounded the antennas, I was getting sparks when I connected the radio ground (at internal, 'house ground' potential) to the antenna ground (outside, true earth potential).
I rent this house with my friend, from his mom and stepdad. His stepdad (an electrician, though it's been a few years since he did any real work)came over today and we spent about four hours troubleshooting.
Here's the lowdown.
We're measuring about 20 V AC from hot to ground and 14-15 V AC from neutral to ground on this circuit. All other circuits have 0 (or less than 0.1) V AC from hot-ground and neutral-ground.
The only things on this circuit that we can identify:
Three outlets in my room
a fishtank in the kitchen
a small attic vent fan
The problem exists even after disconnecting everything in my room, the fishtank pump *and* the attic fan.
We've redone the breaker box grounds and double-checked all accessible junction boxes and lines for any weird stuff hanging off it, or wiring flaws - have found none.
Our next step is just to put in a virgin run of 12/3 (or whatever the hell is most appropriate) from the junction box to my room. This will be a six-hour PITA job, because the breaker box is on an outside wall, and the roof has a very low pitch (read: we can't get to the last few feet of in-attic horizontal run before it turns down for the JB).
House is approx. 30 years old, your typical ranch home of the 70's.
Any thoughts on other stuff we can check before we run a new circuit?
Well, once I grounded the antennas, I was getting sparks when I connected the radio ground (at internal, 'house ground' potential) to the antenna ground (outside, true earth potential).
I rent this house with my friend, from his mom and stepdad. His stepdad (an electrician, though it's been a few years since he did any real work)came over today and we spent about four hours troubleshooting.
Here's the lowdown.
We're measuring about 20 V AC from hot to ground and 14-15 V AC from neutral to ground on this circuit. All other circuits have 0 (or less than 0.1) V AC from hot-ground and neutral-ground.
The only things on this circuit that we can identify:
Three outlets in my room
a fishtank in the kitchen
a small attic vent fan
The problem exists even after disconnecting everything in my room, the fishtank pump *and* the attic fan.
We've redone the breaker box grounds and double-checked all accessible junction boxes and lines for any weird stuff hanging off it, or wiring flaws - have found none.
Our next step is just to put in a virgin run of 12/3 (or whatever the hell is most appropriate) from the junction box to my room. This will be a six-hour PITA job, because the breaker box is on an outside wall, and the roof has a very low pitch (read: we can't get to the last few feet of in-attic horizontal run before it turns down for the JB).
House is approx. 30 years old, your typical ranch home of the 70's.
Any thoughts on other stuff we can check before we run a new circuit?